MV100 ELECTRIC CONTROLLERS T100, T200 THERMOSTATIC CONTROLLERS AND V2000 RADIATOR VALVES

62-3048—2

10

Table 6. T100 and T200 Settings and Corresponding Temperatures in °F (°C).

a

Setting not marked on dial.

Setpoint Locking or Limiting

(T100A,F,M only)

A single temperature or range-limiting lock is available for the

T100A,F,M. See Accessories in the Specifications section.

Refer to the T100A,F,M Installation Instructions for procedural

details.

Cartridge Replacement

With the appropriate tools, the V2000 cartridge can be

replaced while under pressure.

WARNING

Severe Scalding Hazard.

Contact with hot liquid can lead to severe injury

or cause death.

For a pressurized valve, only open with Valve Cartridge

Replacement Tool.

CAUTION

Hot Surface Hazard.

Contact with hot valve body can cause

severe burning.

Service cartridge only when valve body is cool.

CAUTION

Hazardous Splashing Fluids.

Can injure, burn, or blind.

Wear safety glasses or goggles.

Under Pressure

Replacing the V100 Cartridge with the system under pressure

requires the Valve Cartridge Replacement Tool (see

Accessories in the Specifications section). See Pressurized

Valve Cartridge Replacement section for details.

Not Under Pressure

Replacing the cartridge without the Valve Cartridge

Replacement Tool requires one of the following:

• Isolation of valve from system pressure.

• System shutdown and drain to valve level.

Once the valve is not pressurized:

1. Using a 3/4 in. (19 mm) hex (6- or 12-point) socket

wrench, remove and discard the cartridge.

2. Clean the inside of valve and cartridge sealing surfaces.

Install a new cartridge.

NOTE: Torque cartridge to 25 ft-lb.

SINGLE-PIPE STEAM APPLICATIONS

Many older buildings original heating systems were

single-pipe steam. The advantage of single-pipe steam

systems is lower initial cost, resulting from the use of less

piping and elimination of radiator steam traps.

CAUTION

Boiler Flooding Hazard.

Loss of system control and boiler damage can

result.

For a one-pipe steam system radiator, install valve only

at the vent location.

IMPORTANT

Ensure vacuum breakers are installed on the steam

system risers. If vacuum breakers (that open to the

atmosphere at zero psig) are not installed, the system

can develop a negative pressure and pull steam back

into the radiators on resumption of steam.

Refer to Fig. 12 for installing the one-pipe steam radiator

adapter assembly.

Single-Pipe Steam Systems

T100/V2043H (with vent) operation to provide temperature

control for a formerly uncontrolled single-pipe steam system

follows:

1. The boiler is off (zero steam pressure); radiators are

filled with air; the vent is open.

2. The T100 calls for heat, opening the valve.

3. At the command of an external controller (such as a

representative zone thermostat, or a timer controlled by

outside temperature) the boiler cycles on and begins

delivering steam to the system.

4. Steam enters the radiator, forcing air through the open

V2042H and out through the vent.

5. Once the air is exhausted, the steam heats the

thermostatic element of the vent, causing it to close.

6. The steam cools forming condensation. Condensation

flows out of the radiator making room for more steam to

enter.

7. The T100 is eventually satisfied (temperature equals the

setpoint) and it closes the V2042H.

8. The air in the system (introduced by the vacuum

breakers) begins to fill the radiator. The air in the radiator

prevents steam from coming in and the radiator cools.

9. The boiler cycles off by command of components

external to the T100/V2042H and the steam pressure

returns to zero.

0

*

1

2

3

4

5

6

T100A,F

32 (0)

43 (6)

46 (8)

54 (12)

61 (16)

68 (20)

73 (23)

79 (26)

T100B,C

55 (13)

61 (16)

64 (18)

68 (20)

72 (22)

75 (24)

79 (26)

a

T100M

43 (6)

61 (16)

64 (18)

68 (20)

72 (22)

75 (24)

a

79 (26)

a

T200

43 (6)

52 (11)

57 (14)

63 (17)

68 (20)

73 (23)

79 (26)