Reset to default settings, Keypad lock, Troubleshooting – Aube Technologies Programmable Wall T1073 User Manual
Page 2: Specifications, Warranty, Technical assistance, 2 time menu, 3 configuration menu, 4 program menu, 2 sec
TI073
400-073-000-A 2009-01-28 2/2
5.2
Time Menu
The time display flashes on the screen when the time has not yet been
set or after a 4-hour power outage. Use the Time menu to select the
time format (12-hour or 24-hour) and to set the clock and date.
NOTE: The date is used to determine the sunset and sunrise times.
5.3
Configuration Menu
(Conf)
Use the Configuration menu to set the following parameters (see
sections 5.3.1 to 5.3.4).
5.3.1 Backlight mode (SCRN)
The screen is lit at high intensity for 8 seconds when you press any
button. The rest of the time, depending on the backlight mode
selected, the screen behaves as follows:
Scrn Off: The screen is not lit.
Scrn On HI: The screen is lit at high intensity.
Scrn On LO: The screen is lit at low intensity (default mode).
5.3.2 Automatic Daylight Savings Time Changeover (DLS)
When automatic daylight savings time changeover is on (DLS On), the
TI073 changes to daylight savings time (summer time) at 2:00 am on
the second Sunday of March and changes back to normal time (winter
time) at 2:00 am on the first Sunday of November. This function is
enabled (DLS On) by default.
5.3.3 Latitude and Longitude Coordinates (LAT and LONG)
The coordinates are used to turn the lights on at sunset and off at sun-
rise. The latitude is set to +45 and longitude to -75 by default. These
settings provide approximate sunset and sunrise times for most North
American cities. To obtain your city’s coordinates (or those of a nearby
city), see the coordinates table. You can also obtain this information at
www.aubetech.com/timer or with a Global Positioning System (GPS)
device. The accuracy of the sunset and sunrise times depends on the
accuracy of the coordinates you enter for your city.
NOTE: Enter a negative value for a south latitude or a west longitude.
5.3.4 Correction Factor (ADJ)
If your city’s time zone is based on political or economic boundaries
instead of its coordinates, your lights might switch on or off too early or
too late with respect to sunrise and sunset. In this case, apply a
correction factor (+1 or -1 hour; refer to addendum). Otherwise, leave
it at 0 (default value).
5.4
Program Menu
(Prog)
Use the Program menu to set the programs; i.e. the times you want
the lights to turn On or Off when the switch is in Automatic mode. To
set a program, proceed as follows:
n
Select a program number (see section 5.4.1)
o
Set the day(s) of the program (see section 5.4.2)
p
Set the program start time (see section 5.4.3)
5.4.1 Selecting a program number
You can set up to 21 “On” programs
(“P01 On” to “P21 On”) and 21 “Off”
programs (“P01 Off” to “P21 Off”).
Select an “On” program to set when to
turn the lights on. Select an “Off”
program to set when to turn the lights
off.
5.4.2 Setting the day(s) of the program
After selecting a program, set the day(s) of the program. You can
select a specific day, all 7 days or “none”. Choose “none” for any
unused program.
5.4.3 Setting the program start time
After setting the day(s) of the program, set its start time. You can
select either a specific time, the sunset time or the sunrise time:
•
To select a specific time:
(1) Advance to the hour setting and select the hour.
(2) Advance to the minutes setting and select the minutes.
•
To select sunset or sunrise time:
(1) Advance to the hour setting and select the sunset time or
sunrise time. (When you scroll, the sunset time and
sunrise time
appear between 11 pm and 12 am.)
(2) To enter an offset (from -70 to +70 minutes in 10-minute
increments) between the sunset or sunrise time and the
program start time, advance to the minutes setting and change
the minutes.
•
EXAMPLE: If the sunset time is 6:13 pm and you change the
minutes to display 6:43 pm, you have entered a delay of 30
minutes. If, later in the year, the sunset time is 4:01 pm, the
program will start at 4:31 pm.
•
NOTE: When you enter an offset,
appears along with
or
when you display the sunset or sunrise time. To remove the
offset, display the sunset or sunrise time and change the minutes
until
disappears.
5.4.4 Examples
Example 1: The lights turn on at sunset and off at 11:00 pm every day
(default setting).
Example 2: The lights turn on at sunset and off at sunrise every day.
Example 3: The lights turn on at 8:00 pm every day and turn off at 10:00
pm every day except on Saturday night when they turn off at 1:00 am.
Be careful about overlapping!
For example, if you set “P01 Off” at 10:00 pm for all 7 days and set “P02
Off” to 11:00 pm for Saturday, on Saturday, the lights will turn off at 10:00
pm, not 11:00 pm, since “P01 Off” is set to an earlier time than “P02 Off”.
To return the switch to its default settings,
simultaneously press both main and left buttons and
hold. The software version will appear for 5 seconds.
RST will appear for the next 5 seconds. Release the
buttons when all segments appear on the screen. The
switch is now reset (see default settings in the menu
flowchart).
When the keypad is locked, the
icon appears on the screen and the
only change permitted is the changing of the state. For example, if the
lights are off, they will turn on when you press the main button.
However, in Automatic mode, the default state for the current program
will be overridden until the next program starts. If you press the main
button again before the start of the next program, the lights return to
their initial state. To lock or unlock the keypad, press the buttons
in the following order:
NOTE: You must perform the whole procedure in an interval of 2
seconds. If the procedure was not properly performed, wait another 2
seconds before retrying.
Supply
: 120 VAC, 60 Hz
Minimum load
: 40 watts
Maximum load
: 500 watts
Operating temperature range
: -15 °C to 50 °C (5 °F to 122 °F)
Storage temperature range
: -40 °C to 60 °C (-40 °F to 140 °F)
Power outage
: The screen is blank. Only the time must be set if the outage
lasts more than 4 hours; all other settings and programs are permanently
saved.
Latitude range
: from -65° to +65°
Solar table precision
: +/- 11 min. (within ±60° latitude)
Certification
: UL (c UL us)
AUBE warrants this product, excluding battery, to be free from defects in the work-
manship or materials, under normal use and service, for a period of three (3)
years from the date of purchase by the consumer. If at any time during the war-
ranty period the product is determined to be defective or malfunctions, AUBE shall
repair or replace it (at AUBE's option).
If the product is defective,
(i)
return it, with a bill of sale or other dated proof of purchase, to the place
from which you purchased it, or
(ii)
contact AUBE. AUBE will make the determination whether the product
should be returned, or whether a replacement product can be sent to you.
This warranty does not cover removal or reinstallation costs. This warranty shall
not apply if it is shown by AUBE that the defect or malfunction was caused by
damage which occurred while the product was in the possession of a consumer.
AUBE's sole responsibility shall be to repair or replace the product within the
terms stated above. AUBE SHALL NOT BE LIABLE FOR ANY LOSS OR DAM-
AGE OF ANY KIND, INCLUDING ANY INCIDENTAL OR CONSEQUENTIAL
DAMAGES RESULTING, DIRECTLY OR INDIRECTLY, FROM ANY BREACH OF
ANY WARRANTY, EXPRESS OR IMPLIED, OR ANY OTHER FAILURE OF THIS
PRODUCT. Some provinces, states or regions do not allow the exclusion or limita-
tion of incidental or consequential damages, so this limitation may not apply to
you.
THIS WARRANTY IS THE ONLY EXPRESS WARRANTY AUBE MAKES ON
THIS PRODUCT. THE DURATION OF ANY IMPLIED WARRANTIES, INCLUD-
ING THE WARRANTIES OF MERCHANTABILITY AND FITNESS FOR A PAR-
TICULAR PURPOSE, IS HEREBY LIMITED TO THE THREE-YEAR DURATION
OF THIS WARRANTY. Some provinces, states or regions do not allow limitations
on how long an implied warranty lasts, so the above limitation may not apply to
you.
This warranty gives you specific legal rights, and you may have other rights which
vary according to the province, state or region.
705 Montrichard Avenue
Saint-Jean-sur-Richelieu, Quebec
J2X 5K8
Canada
Tel.: (450) 358-4600
Toll-free: 1-800-831-AUBE
Fax: (450) 358-4650
Email: [email protected]
For more information on our products, go to
www.aubetech.com
“P01 On” “P01 Off”
Program
Days
Time
Program
Days
Time
P01 On
All 7
days
sunset
P01 Off
All 7
days
11:00
pm
P02 On to
P07 On
None
—
P02 Off to
P07 Off
None
—
Program
Days
Time
Program
Days
Time
P01 On
All 7
days
sunset
P01 Off
All 7
days
sunrise
P02 On to
P07 On
None
—
P02 Off to
P07 Off
None
—
Program
Days
Time
Program
Days
Time
P01 On
All 7 days
8:00 pm
P01 Off
Sunday (Su)
10:00 pm
P02 On
None
—
P02 Off
Monday (Mo)
10:00 pm
P03 On
None
—
P03 Off
Tuesday (Tu)
10:00 pm
P04 On
None
—
P04 Off
Wednesday (We)
10:00 pm
P05 On
None
—
P05 Off
Thursday (Th)
10:00 pm
P06 On
None
—
P06 Off
Friday (Fr)
10:00 pm
P07 On
None
—
P07 Off
Sunday (Su)
1:00 am
s
Reset to Default Settings
6.
t
Keypad Lock
7.
2 sec.
u
Troubleshooting
8.
The screen is blank.
• A light bulb is burned out.
• The safety switch is pulled out (see section
4).
The display is faded or
irregular.
• The load is less than 40 W.
• The ambient temperature is either below or
above the switch’s operating temperature.
The metal plate is hot.
This is normal with high loads (maximum of
500 W).
The sunset or sunrise
time is inaccurate.
• The date or time is wrong
(see section 5.2).
• The longitude or latitude is wrong
(see section 5.3.3).
• The correction factor is wrong
(see section 5.3.4).
• You have entered an offset
(see section 5.4.3).
v
Specifications
9.
;
Warranty
10.
Technical Assistance
11.