Related information, Remove the motherboard assembly – FUJITSU SPARC T5120 User Manual

Page 144

Advertising
background image

118

SPARC Enterprise T5120 and T5220 Servers Service Manual • July 2009

Note –

The firmware configuration variable settings are not stored in the SCC

module. If you replace the motherboard, these settings will become the factory
default settings. If possible, keep a record of any firmware variables that have been
changed from the factory default values so you can configure the new motherboard
with those settings.

Related Information

■

“Remove the Motherboard Assembly” on page 118

■

“Install the Motherboard Assembly” on page 120

▼ Remove the Motherboard Assembly

Caution –

This procedure requires that you handle components that are sensitive to

electrostatic discharge. This discharge can cause server components to fail.

1. Run the ALOM CMT showrc command and make a note of any SP variables

that have been modified from the factory default.

2. Stop Solaris OS to get the OpenBoot PROM prompt.

3. Run the printenv command to make a note of any OpenBoot PROM variables

that have been modified

4. Power off the server.

See

“Removing Power From the System” on page 60

.

5. Remove the server from the rack.

See

“Remove the Server From the Rack” on page 64

.

6. Attach an antistatic wrist strap.

7. Remove the top cover.

See

“Remove the Top Cover” on page 67

.

8. Remove the air duct.

See

“Remove the Air Duct” on page 100

.

9. Remove all PCIe/XAUI riser assemblies.

See

“Remove a PCIe/XAUI Riser” on page 102

.