Fault diagnostics, Transmitter adjustment, 3 electrical connection 0 v output signal – WIKA T91.30 User Manual

Page 2: 2 thermocouple input, 1 preparation, 2 adjustment, 3 closing steps

Advertising
background image

230 VAC

24 VDC

Load

(PLC, PC)

Thermocouple

C_212-232.01

Zero

Span

8

7

6

2

3

4.3 Electrical connection 0 ... 10 V output signal

Pt100

230 VAC

24 VDC

Load

(PLC, PC)

8

7

6

1

3 4

C_254.01

Span

Zero

Model T91.30.254
Pt100 in 2- or 3-wire connection.
With a 2-wire connection, the resistance of the input leads affects
the measurement results. Therefore this connection should only
be selected if the wires are short, or accuracy requirements are
low. If using a 2-wire connection, always connect a jumper
between input terminals 3 and 4.

Model T91.30.232
The positive lead of the thermocouple is connected to terminal 3
on the transmitter and the negative lead to terminal 2.
The transmitter is galvanically isolated between input and output;
so non-isolated thermocouples can therefore be used.

4.2 Thermocouple input

Model T91.30.212
The positive lead of the thermocouple is connected to terminal 3
on the transmitter and the negative lead to terminal 2.
The output voltage follows the applied input voltage linearly.
There should be no galvanic coupling between the sensor and the
supply or output voltage.

5.1 Preparation

Connect a suitable simulation source to the input of the T91
(Pt100 or thermocouple simulator). When simulating a Pt100,
connect the simulator in a 2-, 3- or 4-wire configuration.
We recommend the use of passive resistances.
When simulating a thermocouple, the actual terminal temperature
of the transmitter must be pre-set on the simulator (Cold Junction
Compensation).

T

Connect a multimeter to the 0 … 10 V output signal

T

Connect a suitable power supply to the transmitter

5.2 Adjustment

1) Set the simulator with approx. 1 V offset from the lower limit of

the measuring range. (e.g. -20 °C = 1 V for a measurement
range -30 ... +70 °C)

2) Turn the zero potentiometer Z, until the output signal (in our

example -20 °C = 1 V output signal) matches the desired value

3) Set the simulator to the upper limit of the measuring range ,

e.g. +70 °C for measurement range -30 ... +70 °C

4) Turn the span potentiometer S, until the output signal (in our

example 70 °C = 10 V) matches the desired value

5) Repeat step 1 and check signal (1 V)
6) Repeat step 3 and check signal (10 V)

5.3 Closing steps

Disconnect the simulator, the multimeter and the power supply

6. Fault diagnostics

When measuring with resistance thermometers or thermocouples,
factors arising from the design and measuring technology used
can falsify the results measured. The most important effects that
can lead to faults are listed below:

Error

Possible cause

No voltage output

- No supply voltage
- Display unit not working
- Circuit interruption in the supply line

Output signal
1) 0 V

- Short circuit in the Pt100

2) corresponds to room temperature

- Short circuit in the thermocouple

Output signal

- Sensor break

> 10 V
Temperature read out

- Poor lead insulation resistance

too low/fluctuates
Read out obviously

- Moisture in the sensor or in the senor

too high or too low

wire

- Not correct compensation wire or

incorrect thermocouple

If the measuring point is

- Thermocouple polarity incorrect

heated up the output signal
reduces
When only one pole of the

- Electromagnetic disturbances are

thermocouple is connected,

coupled to the input lead

a value is still displayed

- Through poor galvanic isolation, and

poor insulation, parasitic voltages are
present, e.g. through the thermal
insulation

Displayed value obviously

- Electromagnetic disturbances are

incorrect

coupled to the input lead

- Parasitic galvanic voltages, e.g. as a

result of moisture in the compensation
cable insulation

5. Transmitter adjustment

Zero point and Span adjustment is carried out via potentiometers.
These are under the transparent cover. To open the transparent
cover, it must be pressed inwards on its shortest sides and pulled
away carefully. The potentiometers are protected against
accidental alteration.
The zero-point potentiometer can be adjusted to make small
corrections. After any adjustment of the span potentiometer, a
complete adjustment of the transmitter is necessary.

Maximum power supply: 15 …35 VDC

(reverse-polarity protected)

The output voltage follows the applied input signal linearly.
Please note that the output can only be regulated to within
approx. 0.02 V at the lower supply voltage.

Model

Terminals

T91.30

6 (+signal), 8 (+24 V), 7 (-GND)