SPECIFICATIONS

Operating Conditions:

0 °C to 50 °C ( 32 °F to 122 °F )
0% to 95% R.H. non-condensing

Sensor:

Local 47 K NTC thermistor

Resolution:

± 0.1 °C ( ± 0.2 °F )

Control accuracy:

( calibrated )

± 0.2 ° C ( ± 0.4 °F ) for low ranges
± 0.9 ° C ( ± 1.8 °F ) for high ranges

Ranges:

10 °C to 32 °C ( 50 °F to 90 °F )

-18 °C to 82 °C ( 0 °F to 180 °F )

Outputs:

Isolated Triac: 30 Vac at ½ A max.
0 to 10 Vdc into 2K

Ω resistance min.

0 / 5 Vdc at 20 mA max. for both outputs.

Power:

24 Vac -15%, +10% 50/60 Hz; 2 VA

ORDER CODE

T211

-

AB

-

CD

-

EF

( without day-night mode )

T261

-

AB

-

CD

-

EF

( with day-night mode )

A

Output no. 1 ( controlled device )

Type

1

Relay, thermal relay, two position motor

Isolated Triac

2

Normally open thermal valve

Isolated Triac

3

Normally close thermal valve

Isolated Triac

4

"SSR" with 24 Vac input

Isolated Triac

5

"SSR" with 3-32 Vdc input

Pulsed 0/5 Vdc

B

Output no. 2 ( controlled device )

Type

1

Relay, thermal relay, two position motor

Isolated Triac

2

Normally open thermal valve

Isolated Triac

3

Normally close thermal valve

Isolated Triac

4

"SSR" with 24 Vac input

Isolated Triac

5

"SSR" with 3-32 Vdc input

Pulsed 0/5 Vdc

C

Output no. 1 and 2 control mode

1

Heating, reverse acting, ( RA )

∗ Standard

2

Cooling, direct acting, ( DA )

3

Heating, RA ( no. 1 ) and cooling, DA ( no. 2 )

4

Cooling, DA ( no. 1 ) and heating, RA ( no. 2 )

D

Main control sensor location

1

Room, inside thermostat, or ( duct return air**)

∗ Standard

2

Duct supply air **

** Order with S60 or S70 sensor

E

Setpoint adjustment

1

User adjustable

∗ Standard

2

Blind cover

F

Scale

1

10

°C to 32 °C

∗ Standard

2

50

°F to 90 °F

3

-18

°C to 82 °C

∆

4

0

°F to 180 °F

∆

Example: T261 - 53 - 31 - 12
One "SSR" 3-32 Volts heating output
and one normally close thermal valve cooling output.
Main sensor located inside the room
Adjustable setpoint. Scale 50

°F to 90 °F.

The output no. 3 is a cooling signal for damper modulation.

∆ Note: These models have a vertical cover.

Note: Order remote sensors separately

WIRING

NOTE: WITH THE PROPER CODES, TERMINALS 5, 6, 8 AND 9 CAN BE

WIRED TOGETHER BETWEEN EACH THERMOSTAT IF POLARITY IS RESPECTED

Power supply 24 Vac -15% +10%

50/60 HZ 2 VA

COMMON

24 VAC

24VAC

5
6

POWER SUPPLY 24 Vac.

IMPORTANT: IF USING A COMMON TRANSFORMER
RESPECT POLARITY (COMMON AND 24 VAC)
BETWEEN EACH THERMOSTAT

Day night mode T261 only

CLOSE =

NIGHT

SET BACK

COMMON

INPUT

DAY / NIGHT 6

8

DAY NIGHT MODE

1 CONTACT USED FOR ALL

THERMOSTAT USING THE

SAME TRANSFORMER

Output #1 code A= 1, 2, 3 & 4 Triacs

Output #2 code B= 1, 2, 3 & 4 Triacs

RELAY OR THERMAL

VALVE 24 VAC

CONTACT

OUTPUT

1
2

OUTPUT #1 AND/OR #2 USING RELAY WITH ISOLATED TRANSFORMER

R

24VAC

3
4

AND / OR

USE TERMINALS 3 & 4 FOR OUTPUT #1
USE TERMINALS 1 & 2 FOR OUTPUT #2

Power limit input

Analog 0 to 10 Vdc

LIMIT INPUT

0 TO 10 Vdc

COMMON

0 TO 10 Vdc

6

9

POWER LIMIT INPUT USING 0 TO 10 Vdc

ENERGY

SYSTEM

MANAGEMENT

Output #1 code A= 1, 2, 3 & 4 Triacs

Output #2 code B= 1, 2, 3 & 4 Triacs

RELAY OR

24 VAC

THERMAL VALVE

CONTACT

OUTPUT

COMMON

24 VAC

24VAC

5

6

OUTPUT #1 AND/OR #2 USING SAME TRANSFORMER TO OUTPUT

3

4

AND / OR

1
2

USE TERMINALS 3 & 4 FOR OUTPUT #1
USE TERMINALS 1 & 2 FOR OUTPUT #2

Output #1 code A= 5 Pulsed 0/5 Vdc

Output #2 code B= 5 Pulsed 0/5 Vdc

SOLID STATE

RELAY

3-32 VDC
TRIGGER

LOAD

COMMON

0/5 V

6

OUTPUT #1 AND/OR #2 USING PULSED 0/5 Vdc

AND / OR

2

4

USE TERMINALS 4 & 6 FOR OUTPUT #1
USE TERMINALS 2 & 6 FOR OUTPUT #2

Output #3 Analog 0 to 10 Vdc

0 TO 10 VDC

COMMON

0 TO 10 Vdc

6

10

OUTPUT #3 USING 0 TO 10 Vdc

ELECTRONIC ACTUATOR, SCR,
OR VOLTAGE RELAY

Remote main temperature control sensor

Room or return control code D= 1,

Supply control code D=2

EXTERNAL

SENSOR

NOTE: REMOVE

INTERNAL J4 JUMPER

7

REMOTE MAIN CONTROL SENSOR

COMMON

6

VICONICS

DUCT S60 OR S70

ROOM S80

IMMERSION S90

Advertising