Maintenance, Specifications, Wiring diagram – Desa TD100 User Manual
Page 9
![background image](/manuals/75168/9/background.png)
www.desatech.com
118994-01G
9
SPECIFICATIONS
• Rating: High - 36,500 Btu/Hr (10.7 kw)
Low - 0,000 Btu/Hr (5.86 kw)
• Fuel: Propane Vapor Only
• Fuel Consumption/Hour: Min. 0. gal
(0.83 liter), Max. 0.39 gal (1.48 liter)
Min. 0.93 lb (0.4 kg), Max 1.67 lb (0.76 kg)
• Supply Pressure (To Regulator):
Maximum - 00 psi (1,379 Kpa)
Minimum, for input adjustment - 5 psi
(34.5 Kpa)
• Manifold Pressure: High - 1 psi (6.89 kPa),
Low - 0.98 psi (6.77 kPa)
• Ignitor Gap: 0.10"
• Minimum Temperature: -0°F (9°C)
Surrounding Air Temperature
• Heater Size (L x W x H):
18" x 17.15" x 8" (0.45 x 0.43 x .1 m)
• Carton Size (L x W x H):
38.65" x 18.15" x 18" (0.98 x 0.46 x 0.45 m)
• Heater Weight: 96 lb (43.5 kg)
• Shipping Weight: 110 lb (49.9 kg)
MAINTENANCE
WARNING: Never attempt
to service heater while it is
connected to propane/LP supply,
operating, or hot. Severe burns
can occur. Any guard or other
protective device removed for
servicing must be replaced prior
to operating the heater.
1. Keep heater clean. Remove any debris
from ventilation openings.
. Inspect heater before each use. Check
connections for leaks. Apply mixture of
liquid soap and water to connections.
Bubbles forming show a leak that must
be corrected. Correct all leaks at once.
3. Inspect hose/regulator assembly before
each use. If hose is highly worn or cut,
replace it immediately. At least annually,
remove hose/regulator assembly from
heater to inspect entire length of hose.
Replacement hose must be same type
as supplied with unit.
4. Spiders and insects can create a danger-
ous condition that may damage heater or
make it unsafe. Keep burner area clean
of all spiders, webs, or insects.
5. Have heater inspected yearly by a quali-
fied service person.
WIRING dIAGRAM
Gas Light
Burner
Ground
Control Module
Battery
Holder
Black
Orange
Brown
Brown
Brown
White
White
White
Brown
Red
Black
I
S
Electronic
Ignitor
Ignitor Electrode
Ground
ON/OFF
Switch
Control
Valve
Thermocouple
Gas Valve