Test operation, Page 17, Owner's manual – Venstar T0140 User Manual

Page 17: Turn on the power to the heat pump, T0140

Advertising
background image

Page 17

Turn on the power to the Heat Pump.

Test Operation

On the thermostat, slide the Mode Switch
to HEAT. Press the COOLER or WARMER
button until the set temperature is 10 degrees
above room temperature. The HVAC unit
should energize in the heating mode.

Note: You may need to wait up to five minutes
for heating to energize due to the compressor
lockout feature. There is a two minute min-
imum run-time for first stage heating.

On the thermostat, slide the Aux Heat
Switch to the NORMAL position. The
Aux Heat icon will appear indicating that
the thermostat has energized Aux Heat
(page 7).

TWO STAGE OPERATION - The 2nd stage

of heat (auxiliary heat) is turned on when
the room temperature is equal to or less
than: the setpoint minus the 1st stage
deadband (one degree, non-adjustable),
minus the 2nd stage deadband (two
degrees, non-adjustable).

Heat or Cool

Setpoint

Deadband

Deadband

db 1

db 2

1st Stage

turn on

2nd Stage

turn on

Heating

(non-adj. 2 )

Deadband

db 1

1st Stage

turn on

Cooling

(non-adj. 1 )

(non-adj. 1 )