Installation, When installing this product, Location – Honeywell T6570 User Manual

Page 3: Caution

Advertising
background image

T6570, T8570 SERIES DIGITAL FAN-COIL THERMOSTATS

Table 2. Electrical Rating

50-60 Hz

24V 120V 208V 230V 277V

Amps (Resistive)

3.8

3.8

3.8

3.8

3.8

Full Load Inductive

3.0

3.0

1

3.0

3.0

3.0

Pilot Duty

100 VA

1

Equivalent to NEMA 1/8 horsepower rating; allowable load

must be determined by adding nameplate full load and locked

rotor rating of all loads.

Minimum Operational Life (at maximum load): Thermostat

contacts (at 120 Vac): 100,000 cycles

Manual Switches: 10,000 operations.

M12081A

3-11/16

(94)

4-3/16 (122)

1-7/16 (37)

1-1/2

(38)

3-5/16 (84)

2-3/8 (60)

Energy Savings Input: 24 Vdc dry contact, maximum resis-

tance of 1000 ohms. Note 'Caution', page 3.

Protection Class: IP30.

Approvals: CSA Certified C/US LR158158 for Canada and

the U.S.A. Meets CE requirements.

Accessories: Adapter plate for mounting on single- or double-

gang NEMA-standard vertical switch box:

272878 - line voltage models, 24V 2000 series

272881 - 24 V models, 1000 series

T8109 - remote temperature sensor for

T8575D W6380 - fan switching center for T8574/T8575

products

Fig. 1. Nominal dimensions in inches (mm)

INSTALLATION

When Installing this Product...

1. Read these instructions carefully. Failure to follow them

could damage the product or cause a hazardous condi-

tion.

2. Check the ratings given in the instructions and on the

product to make sure the product is suitable for your

application.

3. Installer must be a trained, experienced service techni-

cian.

4. After installation is complete, check out product opera-

tion as provided in these instructions.

CAUTION

Electrical Shock or Equipment Damage Hazard.

Can shock individuals or short equipment circuitry.

Disconnect power supply before installation.

IMPORTANT

T6570 Series are line voltage powered devices.

All wiring must comply with national and local electri-

cal codes, ordinances and regulations.
Provide disconnect means and overload protec-

tion as required.
T8570 Series thermostats
must be powered by an

Approved 24 Vac, Class 2 transformer (such as a

W6380 Relay Control Center).

Location

The T6570, T8570 series thermostats are the temperature

control element in a fan-coil or air-conditioning system. They

must be located about 1.5m (5 ft.) above the floor in a position

with good air circulation to sense room temperature.

The optional T8109 sensor can be used to sense temperature

in return air ductwork, instead of at the thermostat

IMPORTANT

Do not mount device where it can be affected by:

1. Drafts or dead spots behind doors or in corners.

2. Hot or cold air from ducts.

3. Radiant heat from the sun or appliances.

4. Unheated (uncooled) areas such as an outside wall

behind the thermostat.

5. Concealed pipes or chimneys.

3

95C-10897–6