T6570, T8570 SERIES DIGITAL FAN-COIL THERMOSTATS

SINGLE STAGE COOLING

C

23.0

PROPORTIONAL

22.5

BAND

22.0
21.5
21.0

USER

20.5

SETPOINT

20.0

1

1 USER SETPOINT CHANGED

TO 21.5 C (71 F) FROM

SINGLE STAGE HEATING

C

1

23 C (73 F) OR 20 C (68 F).

23.0
22.5

USER
SETPOINT

22.0
21.5
21.0

PROPORTIONAL
BAND

20.5
20.0

M17477

Fig. 4. Single stage control.

AUTOMATIC CHANGEOVER WITH ZERO ENERGY DEADBAND
(SEE FIG. 5)
This type of control is available on auto-changeover models

only. The user setpoint centers on the Zero Energy Deadband.

The cooling switch-off-point is positioned at the bottom end of

the cooling proportional band. Likewise, the heating switch-off

point is positioned at the top end of the heating proportional

band.

Zero Energy Deadband width is selectable in the Installer

Setup mode.

EXAMPLE: Using a deadband of 2°C (4°F) and a user setpoint

of 22°C (72°F), the effective heating setpoint is 21°C (70°F)

and the effective cooling setpoint is 23°C (74°F). A change to

the user setpoint causes both heating and cooling setpoints to

change in parallel. This change is restricted to the minimum

cooling setpoint or maximum heating setpoint limits set within

the Installer Setup mode.

C

COOLING

25.5

PROPORTIONAL

25.0

BAND

24.5
24.0

DEAD

BAND

1

1

USER

23.5

SETPOINT

23.0
22.5

HEATING

22.0

PROPORTIONAL

21.5

BAND

21.0
20.5
20.0

USER SETPOINT CHANGED FROM

22 C (72 F) TO 23.5 C (74 F).

M17478

Fig. 5. Sequence control with deadband.

OPERATING MODES

The thermostat has two main operating modes: Comfort and

Energy Savings. It also has an OFF mode selected by the On/

Off switch.

OFF MODE
When the system switch is set to Off, power is removed from

the thermostat electronics and output terminals, and the

display will go blank. The thermostat will reboot when power is

restored with the On/Off switch.

NOTE: This On/Off switch is a functional switch and should

not be used as an isolating switch.

STARTUP
On first powering up, or after the On/Off switch has been set to

On, the thermostat undergoes a startup and self-checking

sequence: First, all LCD display segments are illuminated to

check the display. Next a number appears to indicate the

software version. The final check is a check of the sensor. On

completion of the startup sequence, after approximately 2

seconds, the thermostat will resume normal control in either

Comfort or Economy mode. On initial power on, the

temperature setpoint defaults are as shown in the following

table. The current setpoint is stored in EEPROM, and if the

thermostat is switched off, then on again, it will resume control

at the last known setpoint.

Table 3. Power Up Default Setpoints

Power Up Default Setpoints

1 relay or heat cool changeover

models

2 relay + cool

sequence models

°C Scale

°F Scale

°C Scale

°F Scale

Setpoint

Default

22

73

22

73

Cooling OFF

point

23

75

Heating OFF

point

21

71

COMFORT MODE
This is the normal operating mode where the thermostat

controls to the setpoint selected by the user. On initial power

up, the user setpoint will return to the last known or default

value. Control action will be determined by either the default

settings or the installer-set parameters. (See page 6)

ENERGY SAVINGS MODE
Energy Savings mode is activated by a dry contact closure on

the special Energy Management System (EMS) input from an

occupancy detector, window contact, etc. If the signal via input

terminals 10 and 11 is calling for Energy Savings mode, then

the thermostat will control to user/installer defined setback

setpoints for increased energy savings. The display will show a

$ symbol to indicate the Energy Savings mode is active.

For example, if the user setpoint is 21°C (70°F) and the Energy

Savings mode setpoint for cooling (unoccupied cooling

setpoint) has been set to 28°C (82°F), then the thermostat

controls to 28°C (82°F) when the input signal activates the

economy mode. There is no user override as long as the EMS

signal is present. The default Energy Savings mode setpoints

are shown in table 4.

The Energy Savings mode input can be configured within the

installer setup mode to be activated by either a short-circuit

(default) or open-circuit signal.

5