Additional switches, User programming modes, Installer setup mode – Honeywell T6570 User Manual

Page 6

Advertising
background image

T6570, T8570 SERIES DIGITAL FAN-COIL THERMOSTATS

Table 4. Energy Saving Mode Default Settings

Energy Savings Mode – Setpoints

Heating Setpoint

Cooling Setpoint

Description

Default

Range

Default

Range

°C Scale

18°C

10-18°C

25°C

25-30°C

°F Scale

65°F

50-65°F

77°F

77-90°F

Additional Switches

FAN SPEED SWITCH (SP3T LINE VOLTAGE)
Where supplied, the fan switch allows the selection of three

different settings: low, medium, or high.

NOTE: The installer should select Constant Fan mode if the

fan motor is a type that does not start reliably at low

speed.

SYSTEM HEAT/COOL SWITCH (SPST LOW VOLTAGE)
Where supplied, this switch signals the microprocessor to

operate the relays in either heating or cooling mode: In heating

mode, the cooling relay is disabled. In cooling mode, the

heating relay is disabled.

User Programming Modes

TEMPERATURE (COMFORT) SETPOINT
The temperature setpoint can be adjusted between 10°C and

30°C in steps of 0.5°C by using the [UP] and [DOWN] keys. If

°F is set within the installer setup mode (see later), the range

will be 50°F to 90°F, adjustable in 1°F steps.

DISPLAY
The measured room temperature is normally displayed (unless

rt = 0 in the installer setup mode), and the first press of the

[UP] or [DOWN] keys will switch to display the user setpoint. If

no key is pressed for 5 seconds, the display will return to

showing the room temperature.

When the cooling relay is closed, this will be indicated by a

(snowflake) symbol, whereas closure of the heating relay will

be indicated by a (flame) symbol.

If there is a wiring problem or the room temperature is less

than 5°C (40°F) or over 38°C (100°F) the display will return a

SF (Sensor Failure) warning. If this warning is not due to a

wiring problem it will disappear once the remote sensor or

thermostat comes within the 4.5 to 37.8°C (40 to 100°F) range.

If the SF warning is due to a faulty remote sensor connection

the thermostat will not transfer measurement to the internal

sensor. To resolve the faulty connection the thermostat must

be powered down, the remote sensor connection must be

removed or fixed and then the thermostat must be re-powered.

Installer Setup Mode

The thermostat allows many of its operating parameters to be

adjusted via an Installer Setup Mode. Each operating

parameter has a two-letter identifier code, which is shown on

the display during the Installer Setup Mode programming

sequence. A description of these is shown in Table 5.

PROGRAMMING PARAMETERS
The installer setup mode is accessed by reducing the setpoint

to 10°C (50°F), waiting 3 seconds or until the room

temperature is displayed, and then pressing the [UP] and

[DOWN] keys simultaneously for 3 seconds.

If the installer setup has previously been entered and the

Minimum Cooling Setpoint increased above 10°C (50°F), the

installer setup mode is accessed by reducing the setpoint to

the new value before pressing the two buttons.

The first parameter identifier will be displayed at this point and

the parameter value can be changed by pressing the [UP] key.

The first press displays the default value and any subsequent

press alters the value. The values will wrap around.

To select the parameter value and move to the next parameter,

press [DOWN]. After the final parameter is selected, a further

press of the [DOWN] key will exit from the programming mode.

PARAMETER VALUES
Each parameter has a default value that is used when the

thermostat is first powered up. This value can be changed from

within the Installer Setup Mode, and once changed, it will be

stored in the EEPROM so it is not lost in the event of power

interruption.

If the user wishes to restore the parameters to the default

values, this can be done by changing the temperature scale tS

from °C to °F (or °F to °C) and back again.

PROGRAMMING EXAMPLE
To enter the installer setup mode:

1. Press to change the temperature setpoint to 10°C

(50°F).

2. Wait 3 seconds, or until the room temperature is dis-

played.

3. Press and hold together until [tS] is displayed.

4. Press once to show the default Temperature Scale

value. Continue to show all possible values of this

parameter in sequence.

5. When the desired value is displayed, it is selected by

pressing once. This will also move to the next parameter,

whose identifier will now be displayed.

6. Continue to use to move from one parameter to the next,

and to alter the parameter value.

7. When the last parameter [rt] has been selected, a final

press of will return the display to its normal operating

mode.

95C-10897–6