Main Menu Buttons -

Humidity

The Humidity feature allows the thermostat to

control a humidifier or use your air conditioner

to dehumidify the space

See: AUX Output Settings on page 39.

Humidification Settings

Humidify with heat - OFF

Adjust Humidify setpoint. (0% - 60%)

When this step is ON, Humidify will only run with a demand for heat.

Run fan - OFF

When this step is ON, the fan will run with a call for Humidification.

Humidify setpoint

Dehumidification Settings

Run A/C to dehumidify - OFF

Adjust Dehumidify setpoint. (25% - 99%)

When this step is ON, the A/C system will be used for Dehumidification.

Maximum Overcool

This specifies how many degrees the A/C system will run past the cool

setpoint to satisfy a demand for Dehumidification. (0-20 degrees F)

Dehumidify setpoint

Humidity

IMPORTANT: Aux Output Usage must be set for Hum or
Dehum for these settings to take effect.

(0%)

(0%)

Reheat - OFF

This turns on electric strip heat during an A/C to dehumidify demand to help

maintain desired room temperatures. (Run A/C to dehumidify must be set to ON

and the GAS ELEC Dip Switch must be set to ELEC - page 52 - to access this feature.

Dehumidify only when cooling - ON

Run dehumidification only when HVAC calls for A/C