56 main menu buttons, Settings, Free cooling – Venstar T7900 User Manual

Page 64: Outdoor air grille hvac unit, Free cooling damper, Continued)

Advertising
background image

56

Main Menu Buttons -

Settings

Free Cooling - DISABLED

Free Cooling - ENABLED

Usable Outdoor Temp

( 65˚)

Turns on Free Cooling.

Free Cooling shuts off above this outdoor temperature. (40 - 80 degrees F)

Free Cooling requires additional dampers and duct work to be installed. Additionally,

the thermostat is wired in a different manner for this feature to function properly.

Before enabling this feature, please make sure these steps are completed.

Mechanical air conditioning is turned on with a 2nd stage demand for cooling

and the Free Cooling, outdoor air damper is closed.

Free Cooling

Mechanical Cooling? - NO

Mechanical Cooling? - YES

If you don’t have a compressor, set Mechanical Cooling to “NO”, Y1 will

then be used to control the Free Cooling Damper(s) and Y2 will be disabled.

If set to “YES”, mechanical (compressor) cooling will be controlled by the

Y2 terminal. (See page 67 for wiring diagram)

Installation Settings

Damper1

Open

Damper2

Closed

Supply

Plenum

Furnace

Air

Filter

Outdoor

AirGrill

Return Air Grill

Coil

AirFlow

AirFlow

AirFlow

AirFlow

AirFlow

Return

Plenum

Barometric

Damper

Free Cooling

Outdoor Air Grille

HVAC Unit

Supply Grilles

Return Grille

Free Cooling

Damper

Return

Damper

Vent to Attic

Barometric

(To relieve building pressure)

(Continued)