Main Menu Buttons -

Settings

Heat Pump Settings

Installation Settings

HP Lockout Outdoor Temp

(65˚)

Heat Pump will not run below this temp. (20 - 75 deg. F)

Aux Heat Lockout - DISABLED

Aux Heat Lockout - ENABLED

Turns on Aux Heat Lockout.

Aux Heat Lockout Temp

(65˚)

Aux Heat will not run above this temp. (0 - 75 deg. F) GAS/EL or HP dip

switch must be set for HP and GAS or ELEC dip switch must be set for ELEC.

Dual Fuel Settings

Dual Fuel - ON/OFF

Changeover With Outdoor - ON/OFF

ON: Uses an outdoor sensor for changeover.

OFF: Uses a third stage heat demand for changeover.


Adjust Balance Point

Choose the temperature for changeover to fossil fuel. (0 - 60 deg. F)

This feature is for heat pump applications only.

This will only appear if the GAS/EL or HP dip switch is set for HP

and the GAS or ELEC dip switch is set for Gas.

When Dual Fuel is ON, an outdoor temperature or, if Change With Outdoor is

set to OFF a demand for third stage heat will be used to stop running the heat

pump and switch to a fossil fuel source of heat. NOTE: Once the change to

fossil fuel is made, the heat demand must finish with fossil fuel. Additional heat

demands within 10 minutes will also use fossil fuel, regardless of outdoor

temperature or stage demand.

Heat Pump Lockout - DISABLED

Heat Pump Lockout - ENABLED

Turns on Heat Pump Lockout.

(Only available

when dip switch

is set for Heat

Pump operation.)

(Continued)