Three-input 240-a power supply leds – Juniper Networks T1600 User Manual

Page 7

Advertising
background image

Table 1: Components Powered by Each Three-Input 240-A Power Supply Input

Two-Input Mode

Three-Input Mode

Input

FPCs in slots

FPC0

and

FPC1

, SIBs, T-CBs,

fan trays, and Routing Engines

T1600-SIBs, T-CBs, fan trays, and
Routing Engines

INPUT 0

FPCs in slots

FPC2

and

FPC7

FPCs in slots

FPC4

through

FPC7

INPUT 1

Not applicable

FPCs in slots

FPC0

through

FPC3

INPUT 2

Three-Input 240-A Power Supply Load Sharing and Fault Tolerance

When the routing node is operating normally and both power supplies are switched
on, load sharing between them occurs automatically. When one power supply fails
or is turned off, the other power supply immediately assumes the entire electrical
load for the system. A single power supply can provide full power for as long as the
routing node is operational. Table 2 on page 7 describes the behavior of the power
supply if one of the inputs fails.

Table 2: Fault Tolerance

Two-Input Mode

Three-Input Mode

Input

If this input fails,

INPUT 0

and

INPUT 1

shut down. The power supply shuts
down, and the other power supply
assumes the electrical load of

INPUT 0

and

INPUT 1

.

If this input fails,

INPUT 0

,

INPUT 1

,

and

INPUT 2

shut down. The power

supply shuts down, and the other
power supply assumes the electrical
load for all three inputs.

INPUT 0

If this input fails,

INPUT 0

is

unaffected and

INPUT 1

shuts down.

The other power supply assumes the
electrical load of

INPUT 1

.

If this input fails,

INPUT 0

is

unaffected and

INPUT 1

and

INPUT 2

shut down. The other power supply
assumes the electrical load of

INPUT 1

and

INPUT 2

.

INPUT 1

Not applicable

If this input fails,

INPUT 0

is

unaffected and

INPUT 1

and

INPUT 2

shut down. The other power supply
assumes the electrical load of

INPUT 1

and

INPUT 2

.

INPUT 2

Three-Input 240-A Power Supply LEDs

LEDs on each power supply faceplate (see Figure 4 on page 8) indicate the status
of the power supply. In addition, a power supply failure triggers the red alarm LED
on the craft interface. Table 3 on page 8 describes the functions of the power supply
LEDs.