T1000 output specifications, T1500 output specifications, T1000 power protection specifications – HP T1000 User Manual
Page 32: T1500 power protection specifications, Voltage specifications, 32 t1500 output specifications, 32 t1000 power protection specifications, 32 t1500 power protection specifications, 32 voltage specifications
Specifications 32
UPS model
Utility voltage
frequency (Hz)
Available settings utility
voltage (VAC)
Branch circuit
rating (A)
Line cord
T1000/1500
NA/JPN/TWN
60/50 100,
110,
120*
15
Nondetachable power
cord with NEMA 5-15
plug
T1000/1500 INTL 50/60
220, 230*, 240
10
Detachable power cord
with IEC-320 plug
T1000 output specifications
UPS model
Output receptacles
Maximum current
T1000
NA/JPN/TWN
8 x NEMA 5-15
8.3 A
T1000 INTL
8 x IEC-320-C13
4.3 A
T1500 output specifications
UPS model
Output receptacles
Maximum current
T1500
NA/JPN/TWN
8 x NEMA 5-15
12.5 A
T1500 INTL
8 x IEC-320-C13
6.5 A
T1000 power protection specifications
UPS model
VA
Nominal power rating (W)
Nominal voltage setting
T1000
NA/JPN/TWN
1000 650
100,
110,
120
T1000 INTL
1000
650
220, 230, 240
T1500 power protection specifications
UPS model
VA
Nominal power rating (W)
Nominal voltage setting
T1500
NA/JPN/TWN
1500 900
100,
110,
120
T1500 INTL
1500
900
220, 230, 240
Voltage specifications
Configuration setting (VAC)
Available nominal output voltage (VAC)
100 100
110 110
120 120
220 220