section 2: poWer supply

availability

Before installing the machine, consider the
availability and proximity of the required
power supply circuit. if an existing circuit
does not meet the requirements for this
machine, a new circuit must be installed.
to minimize the risk of electrocution, fire,
or equipment damage, installation work
and electrical wiring must be done by a
qualified electrician in accordance with all
applicable codes and standards.

circuit requirements

this machine is prewired to operate on
a 110v power supply circuit that has a
verified ground and meets the following
requirements:

nominal voltage ...............................110v
cycle ..................................................60hz
phase ...................................single-phase
minimum circuit size .........................15a

a power supply circuit includes all electri-
cal equipment between the breaker box
or fuse panel in the building and the
machine. the power supply circuit used
for this machine must be sized to safely
handle the full-load current drawn from the
machine for an extended period of time.
(if this machine is connected to a circuit
protected by fuses, use a time delay fuse
marked d.)

note: The circuit requirements listed in
this manual apply to a dedicated circuit—
where only one machine will be running at
a time. If this machine will be connected to
a shared circuit where multiple machines
will be running at the same time, consult a
qualified electrician to ensure that the cir-
cuit is properly sized for safe operation.

Electrocution, fire, or

equipment damage may

occur if machine is not

correctly grounded and

connected to the power

supply.

For your own safety and protection of

property, consult a qualified electrician if

you are unsure about wiring practices or

electrical codes in your area.

full load current rating

the full-load current rating is the amper-
age a machine draws at 100% of the rated
output power. on machines with multiple
motors, this is the amperage drawn by the
largest motor or the sum of all motors and
electrical devices that might operate at
one time during normal operations.

full-load current rating ......... 1.2 amps

the full-load current is not the maximum
amount of amps that the machine will
draw. if the machine is overloaded, it will
draw additional amps beyond the full-load
rating.

if the machine is overloaded for a sufficient
length of time, damage, overheating, or
fire may result—especially if connected to
an undersized circuit. to reduce the risk
of these hazards, avoid overloading the
machine during operation and make sure
it is connected to a power supply circuit
that meets the requirements in the follow-
ing section.