Y2 JUMPER SETTING

If the jumper for MISC1 is set to Y2 the
second stage of cooling.

MISC1 screw terminal on the backplate will control a

Y2 OPERATION - Page 14.4

Control up to two Cool stages.
The 2nd Stage of heat or cool is turned on when:
(A) The 1st Stage has been on for the time required (step #28,
page 14.6).
It is adjustable from 0-60 minutes and the default
is two minutes.

(B) The temperature spread from the setpoint is equal to or greater
than: the setpoint plus the deadband (step #25, page 14.5), plus
the 2nd deadband (step #26, page 14.5).
This 2nd deadband is
adjustable from 0-10 degrees and the default is two degrees.




Page 21.5

Explanation of Jumper Settings

(continued)

And

21

Cool

Setpoint

Deadband

Deadband

db 1

db 2

(adj. 0-10 )

(adj. 1-6 )

1st Stage

turn on

2nd Stage

turn on

Cooling

TEMPERATURE

INCREASE