Installation 24

Before connecting devices, verify that the UPS will not overload by checking that the ratings of the devices

do not exceed the UPS capacity. If the equipment rating is listed in amps, multiply the number of amps by
120 (for Japan, by 100) to determine the VA.
After verifying that the UPS will not overload:

•

Connect the device power cords to the output receptacles on the rear panel of the UPS
(NA/JPN/TWN model).
-or-

•

Connect devices to the output receptacles on the rear panel of the UPS using the jumper cords
included with the UPS (INTL model).

Charging the UPS batteries

Allow the batteries to charge before putting the UPS into service.

IMPORTANT:

Charge the batteries for at least 24 hours before supplying backup power to

devices. The batteries charge to:

•

90% of their capacity within 4 hours

•

100% of their capacity within 24 hours

Powering up the UPS

Press and hold the Power On/Standby button until the UPS beeps. The Power LED illuminates solid green,

indicating that power is available at the UPS output receptacles.

Installing the ERM as a tower

Before installing the unit, review and adhere to all warnings provided in "Precautions (on page