UPS operations 30

UPS operations

Initiating a self-test

A self-test can be performed with equipment connected to the UPS output receptacles. To initiate a self-test,
press and hold the Mute/Test button until the alarm beeps two times.

CAUTION:

Do not unplug the UPS to test the batteries. This action removes safe electrical

grounding and can introduce a damaging surge into the network connections.

The self-test lasts approximately 10 seconds as the UPS switches to battery power to test the load capacity

and battery charge. During the self-test, the Power LED flashes, the Output Load Level LED illuminates, and

the Battery Charge LED illuminates.

Silencing an audible alarm

Press the Mute/Test button.

IMPORTANT:

Although the audible alarm silences, the condition that caused the alarm to sound might still
exist.

If a utility power failure caused the alarm (the Power LED is flashing green), the alarm
silences after power is restored.

Audible alarm conditions

Alarm type

Condition

Audible alarm

Can alarm be
silenced?

Normal

UPS operating from utility power

No audible alarm

N/A

UPS on battery

UPS operating on battery power

On–four short beeps

Yes

Shutdown imminent Batteries nearly out of power

On–continuous

Yes

Battery problem

Batteries must be recharged On–intermittent

beeps Yes

Overload

UPS power capacity exceeded

On–continuous

Yes

Setting the power sensitivity adjustment dial

The power sensitivity adjustment dial is normally set in the counter-clockwise position, enabling the UPS to

provide maximum protection against waveform distortions in the AC input. When distortion occurs, the

UPS provides sine wave power from the battery reserves for as long as the distortion is present. In areas

with poor utility power or where the UPS input power comes from a backup generator, continuous
waveform distortion causes the UPS to switch to battery power. To minimize battery use, experiment with