Using the Dehum Terminal

Press the PROGRAM button to leave the Setup screens. If no buttons are

pressed, the display will leave the setup screens after 30 seconds.

PROGRAM

Press

Normally Closed (NC) =
DEHUM deenergized for
low speed fan.

Normally Open (NO) =
DEHUM energized for
low speed fan.

NC

NO

DeHumidify

Setup

If you configure a MISC output jumper for DEHUM, it may be
programmed to operate in one of two ways:

Dehumidification Notes: The DEHUM terminal will “release” and allow
the fan to operate normally if there is call for 2nd stage cooling or if the call
for Cooling and/or Dehumidification has been satisfied.

PROGRAM

MODE

MODE

Press the MODE button. While holding
the MODE, press the PROGRAM
button to enter Setup screens.

Press the MODE button repeatedly
until this setup screen appears.

Note: Press the

MODE

button momentarily
to move through the
setup screens. Press
and hold the

MODE

button to move back-
wards through the
setup screens.

10

NC

13

2) Normally Open (NO): The thermostat will energize the DEHUM
terminal to allow the fan to run in low speed when there is a call
for 1st stage cooling only and the room humidity is greater than
the dehumidification setpoint.

1) Normally Closed (NC): The thermostat will de-energize the
DEHUM terminal to allow the fan to run in low speed when there
is a call for 1st stage cooling and the room humidity is greater than
the dehumidification setpoint.