Adjusting the deadband – Venstar T2900 User Manual
Page 66
![background image](/files/808457/content/doc066.png)
Page 13.4
13
The above figure assumes the minimum on time for the prior stage has
been met to allow the next stage to turn on; once the deadbands have
been exceeded.
Heat
Setpoint
Cool
Setpoint
Deadband
Deadband
Deadband
Deadband
Deadband
db 1
db 1
db 2
db 2
db 3
(adj. 1-6 )
(adj. 0-10 )
(adj. 0-10 )
(adj. 0-10 )
(adj. 1-6 )
1st Stage
turn on
2nd Stage
turn on
3rd Stage
turn on
1st Stage
turn on
2nd Stage
turn on
Heating
Cooling
TEMPERATURE
DECREASE
INCREASE
Adjusting the Deadband
MULTI-STAGE OPERATION - Controls up to three Heat and two Cool
stages.
The 2nd Stage of heat or cool is turned on when:
And
And
(B) The temperature from the setpoint is equal to or greater
than: the setpoint plus the 1st stage deadband (step #24,
next page), plus the 2nd stage deadband (step #25, next
page) plus the 3rd stage deadband (step #26, next page).
This 3rd stage deadband is adjustable from 0-10 degrees
and the default is two degrees.
(A) The 2nd stage has been on for the time required (step #28,
page 13.6). It is adjustable from 0-60 minutes and the default
is two minutes.
(B) The temperature spread from the setpoint is equal to or greater
than: the setpoint plus the 1st stage deadband (step #24, next
page), plus the 2nd stage deadband (step #25, next page).
This 2nd stage deadband is adjustable from 0-10 degrees and
the default is two degrees.
The 3rd Stage of Heat is turned on when:
(A) The 1st Stage has been on for the time required (step #27,
page 13.6). It is adjustable from 0-60 minutes and the default
is two minutes.