Adjusting the deadband – Venstar T2900 User Manual

Page 66

Advertising
background image

Page 13.4

13

The above figure assumes the minimum on time for the prior stage has
been met to allow the next stage to turn on; once the deadbands have
been exceeded.

Heat

Setpoint

Cool

Setpoint

Deadband

Deadband

Deadband

Deadband

Deadband

db 1

db 1

db 2

db 2

db 3

(adj. 1-6 )

(adj. 0-10 )

(adj. 0-10 )

(adj. 0-10 )

(adj. 1-6 )

1st Stage

turn on

2nd Stage

turn on

3rd Stage

turn on

1st Stage

turn on

2nd Stage

turn on

Heating

Cooling

TEMPERATURE

DECREASE

INCREASE

Adjusting the Deadband

MULTI-STAGE OPERATION - Controls up to three Heat and two Cool
stages.

The 2nd Stage of heat or cool is turned on when:

And

And

(B) The temperature from the setpoint is equal to or greater
than: the setpoint plus the 1st stage deadband (step #24,
next page), plus the 2nd stage deadband (step #25, next
page) plus the 3rd stage deadband (step #26, next page).
This 3rd stage deadband is adjustable from 0-10 degrees
and the default is two degrees.

(A) The 2nd stage has been on for the time required (step #28,
page 13.6).
It is adjustable from 0-60 minutes and the default
is two minutes.

(B) The temperature spread from the setpoint is equal to or greater
than: the setpoint plus the 1st stage deadband (step #24, next
page), plus the 2nd stage deadband (step #25, next page).
This 2nd stage deadband is adjustable from 0-10 degrees and
the default is two degrees.

The 3rd Stage of Heat is turned on when:

(A) The 1st Stage has been on for the time required (step #27,
page 13.6).
It is adjustable from 0-60 minutes and the default
is two minutes.