Explanation of jumper settings, Page 21.3, Prog jumper setting – Venstar T2900 User Manual

Page 97: W3 jumper setting

Advertising
background image

PROG JUMPER SETTING

If the jumper for MISC1, MISC2, or MISC3 is set to PROG,
terminal on the backplate will control a pilot relay or other accessory.

the corresponding MISC screw

Page 21.3

The 3rd Stage of Heat is turned on when:

W3 JUMPER SETTING

If the jumper for MISC1, MISC2, or MISC3 is set to W3, the corresponding MISC screw terminal
on the backplate will control a third stage of heat.

Explanation of Jumper Settings

And

Heat

Setpoint

Cool

Setpoint

Deadband

Deadband

Deadband

Deadband

Deadband

db 1

db 1

db 2

db 2

db 3

(adj. 1-6 )

(adj. 0-10 )

(adj. 0-10 )

(adj. 0-10 )

(adj. 1-6 )

1st Stage

turn on

2nd Stage

turn on

3rd Stage

turn on

1st Stage

turn on

2nd Stage

turn on

Heating

Cooling

TEMPERATURE

DECREASE

INCREASE

W3 MULTI-STAGE OPERATION EXPLAINED - Section 13

This jumper setting allows the MISC outputs to control a pilot relay by time,
temperature, or a signal from the Phone. The following are three possible
scenarios:

PROGRAMMABLE OUTPUT - Section 14

21

(B) The temperature from the setpoint is equal to or greater than: the set-
point plus the 1st stage deadband (step #24, 13.5), plus the 2nd stage
deadband (step #25, 13.5) plus the 3rd stage deadband (step #26,
13.5).
This 3rd stage deadband is adjustable from 0-10 degrees and
the default is two degrees.

(A) The 1st and 2nd stages have been on for the time required (steps #27
and #28, page 13.6).
It is adjustable from 0-60 minutes and the default
is two minutes.

By Temperature: An exhaust fan that needs to energize whenever
the temperature from RS1 rises above 90 degrees F.
By Remote: Remotely arming a security system through the phone.

By Time: A device that requires a start and stop time. For example, an
exterior lighting system that needed to be energized every day
between the hours of 8pm and 1am.