T7350 COMMERCIAL PROGRAMMABLE THERMOSTAT

11

63-4368

Refer to the Light Commercial Building Solution System

Communication Guide form 71-3123 and the E-Bus Wiring

Guidelines, form 74-2865 for a complete description of

network topology rules. Prepare Wiring Diagrams, for wiring

details. Plan to configure each controller. Refer to the Excel

L

ON

S

PEC

™ User Guide, form 74-2937, to configure the

T7350H, XL15 and XL10 Controllers.

Step 1. Plan the System

Plan the use of the T7350H Thermostat according to the job

requirements. Determine the location and functionality of each

device. Verify the sales estimate for the number of other

controllers and devices required. Check the number and type

of other required accessories. When planning the system

layout, consider potential expansion possibilities for future

growth. Planning is very important if HVAC systems and

controllers are to be added in future projects.

Fig. 4. Connecting personal computer to LonWorks® bus.

Step 2. Determine Required Network Devices

A maximum of 60 nodes can communicate on a single

L

ON

W

ORKS®

Bus segment. Each L

ON

W

ORKS®

Bus device

comprises one node. If more than 60 nodes are needed, a

Q7751A Router or Q7740 Repeater is necessary. A router or

repeater allows up to 120 controller nodes per network,

divided between two L

ON

W

ORKS®

Bus segments. Please note

that routers are not supported by the LCBS L

ON

S

PEC

system configuration tool. Refer to the Light Commercial

Building Solution System Communication Guide form 71-3123

for LCBS details. Refer to the E-Bus Wiring Guidelines, form

74-2865, for a complete description of network topology rules

and maximum wire lengths. A 209541B Termination Module

may be required. Refer to the Excel 10 FTT Termination

Module Installation Instructions form, 95-7554.

Step 3. Layout Communications and Power

Wiring:

L

ON

W

ORKS®

Bus Layout

The communications L

ON

W

ORKS®

Bus, is a 78-kilobit network

that uses transformer isolation and differential Manchester

encoding. The Free Topology Transceiver (FTT) L

ON

W

ORKS®

communications Bus supports a polarity insensitive, free

topology wiring scheme, refer to the E-Bus Wiring Guidelines

form, 74-2865, for a complete description of L

ON

W

ORKS®

network topology rules. Fig. 5 shows T7350H devices

connected in a typical free topology L

ON

W

ORKS®

network.

Fig. 5. Typical topology for T7350 devices in L

ON

W

ORKS®

network.

M22492

NOTEBOOK PC

RS-232
SERIAL
PORT

Q7760
SLTA

CABLE
PART
NO. 205979

SHIELDED
INTERFACE
CABLE

T7350H

LonWorks
BUS PORT

NOTEBOOK PC

RS-232

SLTA

SLTA

SLTA

RS-232

RS-232

T7350H

MODEM

MODEM

MODEM

M22493

LonWorks BUS

LonWorks BUS

LonWorks BUS

T7770
WITH NO
LonWorks
BUS ACCESS

T7770

JACK FOR OPERATOR TERMINAL

LonWorks BUS

I/O CONNECTIONS

T7350H

T7350H

T7350H

T7350H

T7350H

T7350H

T7350H

T7350H