T7350 COMMERCIAL PROGRAMMABLE THERMOSTAT

9

63-4368

NETWORK CONFIGURATIONS

The T7350H can be configured to perform a variety of

activities in which data is sent to and/or received from other

nodes on the L

ON

W

ORKS®

network. Information that can be

shared with other network devices includes:

— Current year, month, day, hour, minute, second.

— System mode (HEAT, COOL, AUTO, OFF, EM HEAT).

— Current fan setting (ON, AUTO).

— Space temperature.

— Space relative humidity.

— Discharge air temperature.

— Outdoor air temperature.

— Occupancy sensor status.

— Terminal load.

— Current setpoint.

— Occupied/Unoccupied schedule commands.

— Current occupancy status.

— Occupancy schedule including current occupancy state,

next state and time in minutes until next scheduled

change of occupancy state.

— Relay status (heat/cool stages and fan).

— Alarm status.

— Alarm log including the last five alarms.

— Device Error status.

— Bypass state (multiple XL10 devices follow the bypass

operation of a master device).

A network configuration tool is used to configure the T7350H

Thermostats and other nodes with which the T7350H

interacts. The following is a brief description of the

configurable features that can be commanded over the

network:

• Time Master:

When a T7350H is designated as the network time master,

the current time of day and date is synchronized across the

network every minute. The L

ON

S

PEC

™ T7350H General

Screen can be used to configure a T7350H as the Network

Time Master. Whenever the time of day or date of the time

master is changed, it automatically adjusts all the other

network devices (T7350H, Q7300 & XL15A) bound to the

time master. When a T7350H is controlled by a time

master, the local day light saving schedule is disabled. The

Day Light Saving option on all time master recipients

should be disabled. This prevents erroneous time changes

(local daylight savings switchover) during temporary

network outages.

• Time Schedule:

The occupancy schedule used by a T7350H may reside

locally in that device or remotely in another schedule

device (T7350H, XL15a, XL15b or T7300/Q7300). Local

schedules can be created and modified using the T7350H

keypad, a direct connected PDA, a network connected

configuration tool (L

ON

S

PEC

™) or Command Display.

External schedules can also be modified using the keypad

of the master schedule device, or with a network

connected configuration tool or Workstation. When a

T7350H receives scheduling information over the network,

the user is not prevented from making local schedule

changes at the recipient thermostat. Local schedule

changes (at a recipient device) have no effect on the

scheduling commands received from the master device.

When a T7350H is designated as a master schedule

device, it sends its schedule information (current state,

next state, time until next change of state) to the

appropriate T7350H(s) which, in turn, overrides any

existing internal time schedule. The T7350H Thermostat

can provide master scheduling information to multiple

Excel 10 devices. One T7350H shares the schedule

information (current state, next state, time until next

change of state) with the designated Excel 10 devices.

• System Mode Settings:

System mode settings (HEAT, COOL, AUTO, OFF, EM

HEAT) can be commanded by a remote T7350H or other

compatible XL10 device. A one to many network binding

can be used to command multiple devices from a single

unit. In addition, a network connected Workstation can be

used to change the System Mode.

• Fan Settings:

Fan settings (ON, AUTO) can be changed from a network

connected Workstation.

• Outdoor Air Temperature Sharing:

If a valid outdoor air temperature value is received at the

T7350H OAT network variable input, that value will be used

in the T7350H. The local OAT sensor of the T7350H is

ignored until the network sensor fails.

• Discharge Air Temperature Sharing:

The discharge air temperature value can be shared with

other devices on the network. Note that the T7350H does

not accept a network discharge air temperature input.

• Space Temperature Sharing:

If a valid space temperature value is received at the

T7350H Space Temperature network variable input, that

Source

Destination

T7350H.nvoTime

or

XL15a.nvoTimeOut

Q7300.nvoTime

T7350H.nviTimeSet

or

XL15a.nviTimeIn

Q7300.nviTime

Source

Destination

T7350H.nvoOccSchedule

or

XL15a.nvoTodEventCmd[i]

Q7300.nvoOccSchedulei

T7350H.nviOccSchedule

or

XL10.nviTodEvent

XL15c.nviTodEventIn[i]

Command Source

Command Destination

T7350H.nvoHeatCool

or Workstation

T7350H.nviApplicMode

Source

Destination

Workstation

or Network Tool

T7350H.nviFanAuto

Source

Destination

T7350H.nviOutdoorTemp

or

XL10.nvoOdTemp

XL15c.nvoOdTemp

T7350H.nvoOutdoorTemp

or

XL10.nviOdTemp

XL15c.nviOdTemp

Source

Destination

T7350H.nvoDischAirTemp

XL15c.nviDATemp