T7350 COMMERCIAL PROGRAMMABLE THERMOSTAT

63-4368

24

nvoError Field

Description

errSubBaseVerMisMatch Sub-base/cover firmware mismatch.

0: Sub-base and cover firmware are compatible. (power up value)

1: The firmware version in the sub-base is unable to communicate correctly with the firmware

version of the cover assembly. The cover assembly Public Interface number of the sub-base is not

compatible with the Public Interface number of the sub-base. That is nroT7350Ver.commVer does

not match the version supported by the sub-base. Communications with the sub-base is turned

off.

errNviSpaceTemp

nviSpaceTemp network variable is:

0: either not bound or is bound and being updated periodically (power up value)

1: bound and not being updated periodically (communications or source node failure)

errNviOccSchedule

nviOccSchedule network variable is:

0: either not bound or is bound and being updated periodically (power up value)

1: bound and not being updated periodically (communications or source node failure).

errNviOccSensor

nviOccSensor network variable is:

0: either not bound or is bound and being updated periodically (power up value)

1: bound and not being updated periodically (communications or source node failure)

errNviApplicMode

nviApplicMode network variable is:

0: either not bound or is bound and being updated periodically (power up value)

1: bound and not being updated periodically (communications or source node failure)

errNviOutdoorTemp

nviOutdoorTemp network variable is:

0: either not bound or is bound and being updated periodically (power up value)

1: bound and not being updated periodically (communications or source node failure)

errNviSpaceRH

nviSpaceRH network variable is:

0: either not bound or is bound and being updated periodically (power up value)

1: bound and not being updated periodically (communications or source node failure)

errNviBypass

nviBypass network variable is:

0: either not bound or is bound and being updated periodically (power up value)

1: bound and not being updated periodically (communications or source node failure)

errNviDlcShed

nviDlcShed (Demand Limit Control Shed signal) network variable is:

0: either not bound or is bound and being updated periodically (power up value)

1: bound and not being updated periodically (communications or source node failure)

Table 16.

Reporting T

7350H Errors. (Continued)

T

7350H errors are reported through the manufacturer defined output network variable, nvoError.