Honeywell COMMERCIAL PROGRAMMABLE T7350 User Manual

Page 42

Advertising
background image

T7350 COMMERCIAL PROGRAMMABLE THERMOSTAT

63-4368

42

Table 21. T7350H Network Variable Summary. (Continued)

Nv Name

L

ON

S

PEC

™ Ref Name

Class

Description

nvoStatus

Status

OUT

Status:

Alarm notify disabled:

0: Alarm notification is turned on (power up value).

1: Alarm notification via nvoAlarmH, nvoAlarmLog,

nvoUnitStatus, and nvoStatus has been turned off.

Alarm

0: no alarm (power up value).

1: there is an alarm.

Override the delays associated with automatic control:

0: Delays turned on (power up value).

1: Delays turned off (Useful for troubleshooting).

Invalid ID:

0: The request was for a valid ID (Power up value).

1: The request was not for a valid ID.

Invalid Request:

0: The request was for a valid operation (Power up value).

1: Invalid request for an operation.

Manual control:

0: The function block is in automatic operation (power up

value).

1: The function is in manual operation and outputs respond to

nviManValue.

Status report. Function block number being in status report:

0: Node function block.

1: Space comfort controller function block.

Programming Mode:

0: Normal operating mode (power up value).

1: The node is in the “programming the cover flash memory”

mode, and is not automatically controlling temperature.

Report mask:

0: Normal operation (power up value).

1: RQ_REPORT_MASK received. The status bits that are set

have been implemented.

nvoTerminalLoad

Terminal Load Out

OUT

Terminal load (percent): Reports the demand for supply energy.

Positive numbers are cooling demand and negative numbers are

heating demand. 100 percent is full capacity. Terminal loads

greater than 100 percent or less than -100 percent indicate that

the equipment is not able to supply the required heating or cooling

energy. The valid range is between 163 and minus 163 percent.

Terminal load is used by supervisory level control applications to

reset Boiler or Chiller discharge water temperatures.

163.84: Power up condition.

nvoTime

Time Out

OUT

Current year, month, day, hour, minute, second.

The T7350H can be a time master to other T7350Hs, XL15As, and

Q7300s.