T7350 COMMERCIAL PROGRAMMABLE THERMOSTAT

25

63-4368

APPENDIX D - NETWORK ACCESS TO LOCAL SENSOR DATA

APPENDIX E - SCHEDULING

NETWORK DEVICES

A T7350H can be used to time schedule the following

Honeywell controllers:

• Another T7350H.

• T7300/Q7300.

• XL15C application objects (Control loops/StartStop loops).

• XL10 controllers.

A single T7350 can be configured to schedule all (up to 119)

of the compatible controllers connected to the same network.

This is accomplished by a one to many binding from the

source T7350 to the destination controller or object.

T7350.nvoOccSchedule > XL10.nviOccSchedule.

L

ON

S

PEC

™ automatically implements these NV bindings

based on the selection of Unscheduled Objects (XL10(s),

Q7300(s), T7300H(s) and XL15cAP(s) located on the

L

ON

S

PEC

™ T7350 Scheduling Screen.

APPENDIX F - NETWORK MASTER

CLOCK

A T7350H can be used as the network time master for the

following network connected Honeywell controllers:

• Another T7350H.

• T7300/Q7300.

• XL15A.

This is accomplished by a one to many binding from the

source T7350H to the destination controller. The following is

an example NV binding of one T7350H as a time master to

another.

T7350H.nvoTime > T7350H.nviTimeSet

L

ON

S

PEC

™ automatically implements these NV bindings

based on the selection of Network Time Master check box on

the T7350 General configuration screen. The Day Light

Saving Start and Stop Month on all time master recipients

should be configured to None (invalid). This prevents

erroneous time changes during temporary network outages.

Table 17. T7350H Reports Local Sensor Data.

The T7350H reports local sensor data using the following output network variables.

Nv Name

LonSpec Reference

Name

Description

nvoDischAirTemp Discharge Temperature

Out

The current discharge air temperature. The sensor value source is configured

by nciConfig.dischAirSensor. A value of 327.67 means the sensor is not

functioning correctly or is out of range.

327.67: Power up value

nvoOccSensor

Occupancy Sensor Out

Status of occupancy sensor

0: OC_OCCUPIED

1: OC_UNOCCUPIED

-1: OC_NUL (not configured and power up value)

nvoOutdoorTemp Outdoor Temperature Out

The current outdoor temperature. The sensor value source is specified by

nciConfig.oDAirSensor. A value of 327.67 means the sensor is not functioning

correctly or is out of range.

327.67: Power up value

nvoSpaceRH

Space Humidity Out

The current space humidity. The sensor value source is specified by

nciConfig.humiditySensor. A value of 163.84 means the sensor is not

functioning correctly or is out of range.

163.84: Power up value

nvoSpaceTemp

Space Temperature Out

The current space temperature. The sensor value source is specified by

nciConfig.spaceSensor. A value 327.67 means the sensor is not functioning

correctly or is out of range.

327.67: power up value