T7350 COMMERCIAL PROGRAMMABLE THERMOSTAT

63-4368

36

Table 21. T7350H Network Variable Summary. (Continued)

Nv Name

L

ON

S

PEC

™ Ref Name

Class

Description

nviBypass

Bypass In

IN

Remote time bypass input from usually from another device.

Bypass is a method to command unoccupied override over the

network from another controller. The other controller does the

bypass timing. nviBypass can be used to place the T7350H into

temporary occupied mode. This mode will bypass the time of day

occupancy schedule in this device.

Value State Action

0 NA Do not bypass the time of day

occupancy schedule.

NA 0 or -1 Do not bypass the time of day

occupancy schedule.

0.5 - 100 1 or Bypass the time of day occupancy

greater schedule.

0 0 Mains power up and fail detect value.

nviDlcShed

DLC Shed In

IN

Demand limit duty cycle load shed command from a network

device.

When a shed request is received, the thermostat “bumps” the

control set point up for cooling and down for heating. The amount

of the “bump is a user set point selection. The shed state remains

until a DLC restore command is received or network

communication is lost. When the unit transitions from shed to

restore, the set point is ramped back to the original set point over a

period of 60 minutes. The control only sheds when the thermostat

is in the occupied mode.

Value:

0: No load shed being called (mains power up or failure detect

value).

1 or other values: Call for load shedding.

nviFanAuto

FanOnAuto In

IN

Auto Fan switch (last in wins).

value = 0, state = don’t care:

Fan is On.

value = Don’t care, state = 0 or -1:

Fan is On.

Value = 0.5 - 100: state = 1 or greater:

Fan is On when there is a call for heat / cool.

Failure detect and mains power up value: No change from

previous value.

Value State Action

0 NA Fan is ON.

NA 0 or -1 Fan is ON.

0.5 - 100 1 or Fan is ON when there is a call for

greater heat / cool.

no no Mains power up and fail detect value.

change change

nviFilePos

File Position In

IN

Supports L

ON

M

ARK®

FTP file transfer. Random Access file Pointer

to first byte to be transferred and Number of bytes to transfer.

nviFileReq

File Request In

IN

Supports L

ON

M

ARK®

FTP file transfer. Message request

management is communicated through this input variable.

nviInUse

InUse

IN

In use number is used by a management node to indicate to all

other management nodes that it is “logged on.”