T7350 COMMERCIAL PROGRAMMABLE THERMOSTAT

39

63-4368

Table 21. T7350H Network Variable Summary. (Continued)

Nv Name

L

ON

S

PEC

™ Ref Name

Class

Description

nvoAlarmH

Alarm Out

OUT

Alarm subnet, node and type.

Alarm subnet is the LonWorks subnet number in domain entry to

which nvoAlarmH is bound. If nvoAlarmH is not bound reports

domain index 0.

0: Invalid subnet (power up value).

1-255: Subnet number.

Alarm node is the LonWorks node number (in domain entry to

which nvoAlarmH is bound. If nvoAlarmH is not bound reports

domain index 0).

0: Invalid entry (power up value).

1-127: Node number.

Alarm type is the alarm type being issued:

0: AT_NO_ALARM (power up value).

1: AT_INVALID_SUBBASE_TYPE

2: AT_NETWORK_COMM_FAIL

3: AT_SENSOR_FAIL

4: AT_INVALID_IO_CONFIG

5: AT_COVER_COMM_FAIL

6: AT_COVER_SUBBASE_MISMATCH

-127: AT_rtnINVALID_SUBBASE_TYPE

-126: AT_rtnNETWORK_COMM_FAIL

-125: AT_rtnSENSOR_FAIL

-124: AT_rtnINVALID_IO_CONFIG

-123: AT_rtnCOVER_COMM_FAIL

-122: AT_rtnCOVER_SUBBASE_MISMATCH

-1: AT_ALARM_NOTIFY_DISABLED

nvoAlarmLog

Alarm Log Out

OUT

Reports the last five alarms.

nvoAlarmStatus

Alarm Status Out

OUT

Status of the following alarms states:

Communications between the cover and sub-base.

0: No alarm (power up value).

1: The communications between the thermostat cover

assembly and the sub-base has failed in one or both directions.

The data from the cover to the sub-base has not been received

for at least 90 seconds, or data from the sub-base is not

updating the cover assembly.

Output configuration error:

0: No alarm (power up value).

1: The number of outputs configured exceeds the capability of

the sub-base to support them. Considers sub-base type, heat

pump / conventional application, maxCoolStgs, maxHeatStgs.

Sub-base type error:

0: No alarm (power up value).

1: The sub-base is not a valid sub-base type for the firmware in

the cover assembly.

Network Communications Failure:

0: No alarm (power up value).

1: One of the bound network input variables is not being

updated periodically. This alarm may be caused by a failed

node or a damaged LonWorks network cable.

Sensor failure:

0: No alarm (power up value).

1: One of the analog sensors on the cover assembly has failed

or is out of range (high or low).