T7350 COMMERCIAL PROGRAMMABLE THERMOSTAT

23

63-4368

APPENDIX C - NETWORK ERROR REPORTING

Table 16.

Reporting T

7350H Errors.

T

7350H errors are reported through the manufacturer defined output network variable, nvoError.

nvoError Field

Description

errLoclSpaceSensr

Local space temperature sensor not working.

0: Sensor value is OK. (power up value)

1: Sensor is configured to function and is out of range or disconnected.

errRemtSpaceSensr

Remote space temperature sensor not working.

0: Sensor value is OK. (power up value)

1: Sensor is configured to function and is out of range or disconnected.

errNetSpaceSensr

Network space temperature sensor not working.

0: Sensor value is OK. (power up value)

1: Sensor is configured by the thermostat to function but is not being updated by either the bound

network sensor or by the subbase (faulty subbase).

errLoclHumSensr

Local Humidity sensor not working.

0: Sensor value is OK. (power up value)

1: Sensor is configured to function and is out of range or disconnected.

errRemtHumSensr

Remote Humidity sensor not working.

0: Sensor value is OK. (power up value)

1: Sensor is configured to function and is out of range or disconnected.

errNetHumSensr

Network Humidity sensor not working.

0: Sensor value is OK. (power up value)

1: Sensor is configured by the thermostat to function but is not being updated by either the bound

network sensor or by the subbase (faulty subbase).

errRemtOdSensr

Remote Outdoor air sensor not working.

0: Sensor value is OK. (power up value)

1: Sensor is configured to function and is out of range or disconnected.

errNetOdSensr

Network Outdoor air sensor not working.

0: Sensor value is OK. (power up value)

1: Sensor is configured by the thermostat to function but is not being updated by either the bound

network sensor or by the subbase (faulty subbase).

errRemtSetPt

Remote wall module set point is out of range or disconnected.

0: Value is OK. (power up value)

1: Remote wall module set point is configured to function and is out of range or disconnected.

errDischSensr

Discharge sensor out of range or disconnected.

0: Sensor value is OK. (power up value)

1: Sensor is configured to function and is out of range or disconnected.

errIOConfig

Output configuration error. Considers sub-base type, heat pump / conventional application.

maxCoolStgs, maxHeatStgs.

0: The outputs configuration is consistent with the sub-base type selected (power up value)

1: The number of outputs configured exceeds the capability of the sub-base to support them.

errSubBaseType

Sub-base type error.

0: The sub-base is a valid sub-base type (power up value)

1: The detected sub-base type is not supported by the firmware version of the cover assembly.

errUnused1

Not currently used

errSelfTest

Self test failure. Upon factory test power up, a self test of memory is performed. If external RAM,

EEPROM, or application FLASH memory fails the test, nvoError.errSelfTest is set. This bit is intended

for use in production testing. Field devices should ignore this bit.

0: Passed the test

1: Failed the test

errCoverCommFail

Communications between the cover and sub-base

0: No error (power up value)

1: The communications between the thermostat cover assembly and the sub-base has failed in

one or both directions. The data from the cover to the sub-base has not been received for at least

90 seconds, or data from the sub-base is not updating the cover assembly.