Ups does not provide the expected backup time, Ups emits a slight clicking noise, Power led flashes – HP T2200 User Manual

Page 38

Advertising
background image

Troubleshooting 38

1.

Save your work.

2.

Power down the load devices connected to the UPS output receptacles.

3.

Remove one or more load devices to reduce the power requirements.

4.

Be sure the UPS configuration matches the utility voltage. Refer to "Selecting the UPS voltage
configuration (on page

19

)."

UPS frequently switches between utility and battery
power

Action:

1.

Check the input voltage.

2.

Change the power sensitivity adjustment dial ("

Setting the power sensitivity adjustment dial

" on page

30

) setting.

3.

Contact a qualified electrician to verify that the utility power is suitable for the UPS.

UPS does not provide the expected backup time

Action:

1.

If the Output Load Level LED is red or flashing red, remove one or more load devices to reduce the

power requirements.

2.

Power down the UPS ("

Powering down the UPS

" on page

31

).

3.

Verify that the batteries are connected.

4.

Allow the UPS batteries to charge for 24 hours.

5.

Initiate a self-test ("

Initiating a self-test

" on page

30

).

6.

During extended power outages, save your work, power down the load devices, and then power
down the UPS ("

Powering down the UPS

" on page

31

) to conserve battery power.

UPS emits a slight clicking noise

Action: The UPS is automatically correcting high or low AC voltage on the utility line. No action is

required.

Power LED flashes

Action:
If the Battery Charge LED is also red:

a.

Save your work, and power down the UPS ("

Powering down the UPS

" on page

31

).

b.

After the blackout or brownout is over, power up the UPS ("

Powering up the UPS

" on page

24

).

c.

Allow the UPS batteries to charge for 24 hours.

If the Battery Charge LED is also yellow or green: