Western Telematic MPC-20VS16-3 User Manual
Page 11
1-2
Introduction
Convenient, Durable Design:
The MPC is available with an optional remote display panel, which can be used to show
the status of MPC units installed in hard-to-reach spots, deep inside equipment racks.
When additional outlets are needed, each MPC unit can also be connected to up to
three Auxiliary/Remote MPC units, allowing control of up to 80 outlets via a single IP
Address .
Model Numbers
The MPC series includes a variety of horizontal and vertical models to accommodate the
power distribution needs of almost any rack mount application.
Model No.
Input
Feeds
Input
Voltage
Max. Load
per Outlet
Max. Load
per Input
Max. Load
per Unit
MPC-8H-1
2 ea, 20 Amp
100 to 120 VAC
16 Amps
16 Amps *
32 Amps *
MPC-8H-2
2 ea, 16 Amp
100 to 240 VAC
10 Amps
16 Amps *
32 Amps *
MPC-16H-1
2 ea, 20 Amp
100 to 120 VAC
16 Amps
16 Amps *
32 Amps *
MPC-16H-2
2 ea, 16 Amp
100 to 240 VAC
10 Amps
16 Amps *
32 Amps *
MPC-18H-1
1 ea, 20 Amp
100 to 120 VAC
16 Amps
16 Amps *
16 Amps *
MPC-18H-2
1 ea, 16 Amp
100 to 240 VAC
10 Amps
16 Amps *
16 Amps *
MPC-20V-1
2 ea, 20 Amp
100 to 120 VAC
16 Amps
16 Amps *
32 Amps *
MPC-20V-2
2 ea, 16 Amp
100 to 240 VAC
15 Amps
16 Amps *
32 Amps *
MPC-20VS20-1
1 ea, 20 Amp
100 to 120 VAC
16 Amps
16 Amps *
16 Amps *
MPC-20VS20-2
1 ea, 16 Amp
100 to 240 VAC
15 Amps
16 Amps *
16 Amps *
MPC-20VD20-1
2 ea, 20 Amp
100 to 120 VAC
16 Amps
16 Amps *
32 Amps *
MPC-20VD20-2
2 ea, 20 Amp
100 to 240 VAC
15 Amps
16 Amps *
32 Amps *
MPC-20VS30-1
1 ea, 30 Amp
100 to 120 VAC
20 Amps
24 Amps *
24 Amps *
MPC-20VS30-2
1 ea, 30 Amp
100 to 240 VAC
15 Amps
24 Amps *
24 Amps *
MPC-20VD30-1
2 ea, 30 Amp
100 to 120 VAC
20 Amps
24 Amps *
48 Amps *
MPC-20VD30-2
2 ea, 30 Amp
100 to 240 VAC
15 Amps
24 Amps *
48 Amps *
MPC-20VS16-3
1 ea, 16 Amp
100 to 240 VAC
10 Amps
16 Amps
16 Amps
MPC-20VD16-3
2 ea, 16 Amp
100 to 240 VAC
10 Amps
16 Amps
32 Amps
MPC-20VS32-3
1 ea, 32 Amp
100 to 240 VAC
10 Amps
32 Amps
32 Amps
MPC-20VD32-3
2 ea, 32 Amp
100 to 240 VAC
10 Amps
32 Amps
64 Amps
* In accordance with UL requirements for branch circuits, this value has been
de-rated to 80%.
- MPC Series MPC-20V-1 M MPC-8H-1 MPC-20VS32-3 MPC-20VD20-2 MPC Series MPC-DISPLAY MPC-20VD16-3 MPC-20VS30-1 MPC Series MPC-20V-2 MPC Series MPC-18H-2 MPC Series MPC-16H-1 MPC Series MPC-18H-1 MPC-20VS30-2 MPC Series MPC-8H-1 MPC-20VS20-2 MPC Series MPC-8H-2 MPC Series MPC-16H-2 MPC-20VD32-3 MPC-20VS20-1